I purchased a 2011 Cameo 36FWS in 2018. I immediately noticed that the airflow out the furnace floor ducts was very weak and it took a long time to heat up the camper. I ended up using the electric fireplace and a space heater in 2019.
Upon looking at the furnace setup it was obvious what the problem was: insufficient cold air return ducting to the furnace. Carriage put the furnace in the basement storage area. There is a return duct from the living area to the basement/storage area, and they attempted to seal it off using insulation. This was woefully ineffective as the furnace would pull air not only from the living area, but from the entire basement and storage areas. The basement area is not sealed very well with openings around the slide mechanism and probably other areas with air leaks. The storage area will leak air through the door seals and other siding and construction joints. With those air leaks the furnace is pulling cold outside air into the basement/storage area, as well as return air from the living area.
The furnace needed a dedicated return duct. I considered 2 options. 1. Build a duct passage from the return grill that is under the steps or 2. Use duct boots and flex ducting from the return grill. Both options need an air box around the furnace. I decided on option 1 as I would have had to order the duct boots. In hindsight, it probably would have been easier to do option 2.
I constructed a box around the furnace. I used aluminum angle attached to the hot furnace box. I built a wood frame for the areas away from the hot furnace box. I used fiberglass aluminized duct board for the walls around the furnace, and plywood for the duct from the grill opening under the stairs. The construction was tricky with a lot of trial and error as the duct had to go around the sewer storage pipe and RV structure. Granted, I am not much of a woodworker so it took a while to design and build. The duct was sealed with metal duct tape, expanding foam, and caulk. I also found much air leakage around the furnace duct boots and the end plate, so I sealed those with metal duct tape.
The result was a significant increase in air flow coming out of the ducts and thus heating was much better. The heating in the basement is probably better also, as now no cold air is being drawn in through the slide drive, door and other leaks.